Your browser does not seem to support JavaScript. As a result, your viewing experience will be diminished, and you have been placed in read-only mode.
Please download a browser that supports JavaScript, or enable it if it's disabled (i.e. NoScript).
BTW! same package parsed if its sent and analyzed in Modbus/RTU mode
Hi,
I send the Modbus/ASCII message :3A 30 37 30 33 30 30 33 35 30 30 30 31 43 30 0D 0A
and capture with IO Ninja Serial Tap
Its valid request holding register 0x53 from device 7
Modbus Analyzer is not able to parse this message
Why? is any settings a wrong?
Regards
Juri